I concur with John. This is a complicated topic. You should not design
facilities for fluid collections of any size without input from a fire
protection engineer who has experience with museum fluid preservation issues.
Some of the factors to consider:
* wet-pipe, water-based sprinkler systems (a very aggressive version
if compactors may be used in the space, assuming compact storage is
acceptable to any authorities having jurisdiction)
* good closures for specimen containers to limit alcohol vapor loss
* small rooms to limit the amount of alcohol in a given area, with
actual room sizes based on the maximum capacity of the sprinkler system and
the water supply
* passive features such as fire walls, rated floors and fire
barriers between storage areas
* aggressive ventilation to remove alcohol vapor and prevent a
flammable mixture from occurring in the room air
* hydrocarbon gas detectors rather than smoke detectors in the
storage rooms (no smoke-generating combustibles should be stored in the space
with the collections)
* smoke detectors in return and supply ducts for the ventilation
system
* moderate temperatures (a steady temperature between 65 and 75ºF,
preferably at the low end) with an RH below 65%, but as high as can be
reasonably achieved at the temperature set point (allow RH to drift to maintain
the steady temperature)
* coordination with local authorities-having-jurisdiction (AHJ) on
all aspects of the design and construction of the facility
* restrictions on use of the space for anything other than storage
of the collections (this is NOT where you do research - you need a separate
workroom for that).
As noted above, the critical factor is finding the appropriate expertise.
Let me know if you need suggestions about qualified fire protection
specialists.
Cathy
Catharine Hawks
Conservator
2419 Barbour Road
Falls Church VA 22043-3026 USA
t/f 703.876.9272
mobile 703.200.4370
In a message dated 11/9/2009 11:45:12 P.M. Eastern Standard Time,
simmons.johne at gmail.com writes:
Fire codes do not directly address the storage of museum specimens in
standard museum preservatives. As a result, what is "best practice" varies
from place to place. For example, some institutions are required to use
explosion-proof safety cabinets, some are not; most institutions are required
to have wet pipe sprinkler systems (usually around 0.30 gallons per minute
per square foot capacity), but the required output of the system will vary.
Most fluid specimen storage facilities are required to be above grade and
well-ventilated using floor vents because alcohol is heavier than air
(ventilation systems are usually 1 cubic foot per minute per square foot).
You will have to work with your local fire marshal to get an
interpretation of the regulations that is reasonable and ensures the safety of the
collection and those working with it. In general, you will probably need to
reduce the number of ignition sources in fluid storage areas (e.g., limit wall
sockets, no work activities in fluid storage), reduce the chance of spills
(e.g., earthquake bars on shelves), have a good ventilation system to
prevent the build-up of fumes, restrict access to fluid collection storage, and
so forth.
--John
John E. Simmons
Museologica
128 E. Burnside Street
Bellefonte, Pennsylvania 16823-2010
_simmons.johne at gmail.com_ (mailto:simmons.johne at gmail.com)
303-681-5708
_www.museologica.com_ (http://www.museologica.com/)
and
Adjunct Curator of Collections
Earth and Mineral Science Museum & Art Gallery
Penn State University
19 Deike Building
University Park, Pennsylvania 16802-2709
_jes67 at psu.edu_ (mailto:jes67 at psu.edu)
On Mon, Nov 9, 2009 at 12:02 PM, Stefan Sommer <_Stefan.Sommer at nau.edu_
(mailto:Stefan.Sommer at nau.edu) > wrote:
Dear All,
We are in need of upgrading our alcohol collections infrastructure. We
have significant collections in marine invertebrates, terrestrial arthropods,
fish, amphibians, and reptiles. What is the current 'best practice' for
fire resistant cabinetry and fire suppression systems?
What does your museum use?
Thanks!
Stefan
Dr. Stefan Sommer
Director, Colorado Plateau Biodiversity Center,
_http://www.mpcer.nau.edu/cpbc_ (http://www.mpcer.nau.edu/cpbc)
Executive Producer, A River Reborn, _http://www.mpcer.nau.edu/riverreborn_
(http://www.mpcer.nau.edu/riverreborn)
Faculty Advisor, Grand Canyon SEEDS Chapter,
_http://www.mpcer.nau.edu/seeds_ (http://www.mpcer.nau.edu/seeds)
Board of Directors, Assoc. of College & University Museums & Galleries,
_http://www.acumg.org_ (http://www.acumg.org/)
Faculty, Department of Biological Sciences
Northern Arizona University
Campus Box 5640
Flagstaff, AZ 86011
O: (928) 523-4463
F: (928) 523-7500
H: (928) 214-6324
C: (928) 607-2028
_Stefan.Sommer at nau.edu_ (mailto:Stefan.Sommer at nau.edu)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://mailman.yale.edu/mailman/private/nhcoll-l/attachments/20091110/32583e6b/attachment.html
More information about the Nhcoll-l
mailing list