[Nhcoll-l] Sprinklers in wet collections

Cahawks cahawks at aol.com
Fri May 11 08:46:47 EDT 2012


Rob makes an excellent point. If you do not work closely with local fire protection specialists and have input from a fire protection engineer conversant with the pertinent codes, there is a real risk of making mistakes that are difficult and usually, expensive to rectify. 

There is an excellent chapter on fire protection, including fire protection for fluid collections, in Health and Safety for Museum Professionals. You might want to look at your collection using the risk factors discussed in the chapter.

Cathy 


-----Original Message-----
From: Robert Waller <rw at protectheritage.com>
To: nhcoll-l <nhcoll-l at mailman.yale.edu>
Sent: Thu, May 10, 2012 8:06 pm
Subject: Re: [Nhcoll-l] Sprinklers in wet collections


Hi Gali,
ou have received much good advice and by now you will see there are a number of 
articular options that depend on local codes (and sometimes the even more local 
nterpretation of codes).  Codes in most developed countries have developed to 
e both effective and usually cost effective.  Cooperating fully with your local 
ire code authority is not only the path of least resistance but likely the best 
pproach for the preservation of your collection.
ob
Robert Waller, PhD, CAPC, FIIC
resident and Senior Risk Analyst
rotect Heritage Corp.
22 Simoneau Way
ttawa  ON  K4A 1P4
mail: rw at protectheritage.com
hone: 613-883-2707 (Canada)
hone: 303-872-9739 (USA)
kype: rrwaller
nd,
esearch Associate,
anadian Museum of Nature

----Original Message-----
rom: nhcoll-l-bounces at mailman.yale.edu [mailto:nhcoll-l-bounces at mailman.yale.edu] 
n Behalf Of Paul J. Morris
ent: May-10-12 3:16 PM
o: nhcoll-l at mailman.yale.edu
ubject: Re: [Nhcoll-l] Sprinklers in wet collections
Unfortunately not quite that simple.  
While ethanol as a polar solvent is miscible in water, an ethanol-water mix is 
till flammable down to about 10% ethanol.  With the amount of ethanol now 
raveling by train and truck, large ethanol fires are currently a very active 
opic for training and discussion in the fire service - and it is clear that 
hey are harder to extinguish than gasoline fires.  Pouring something less than 
00 gallons of water on 55 gallons of ethanol might well spread the fire for you 
ather than putting it out.  A single sprinkler head might typically deliver 
round 25 gallons per minute, so there is a good bit of potential for spreading 
 burning ethanol spill before it is diluted enough to be extinguished (thus 
aised door thresholds and ramps might be a good idea, though they might 
ncrease the risk of a spill or be more of a trip hazard than a benefit).  
Sprinklers in a alcohol collection might still be quite effective at supressing 
 fire through their usual methods of breaking down the fire tetrahedron through 
ater removing heat as it vaporises and the resulting large volume of steam 
isplacing oxygen in the air.  
Preventing fires is much better than extinguishing them, so the three pronged 
pproach Andy describes makes good sense to me (noting that absolute ethanol's 
lash point is closer to 55°F, so even lower temperatures might be advisable for 
 collection with substantial amounts of 95% ethanol, and noting that building 
odes are also likely to call for electrical fixtures and devices rated for 
xplosive atmospheres).  
I don't know that either the collections community or the fire service has a 
eally good understanding of what the tradeoffs are in fire protection for wet 
ollections, so there is probably a funding opportunity in here for someone....
-Paul
On Thu, 10 May 2012 14:11:36 +0000
aul Callomon <callomon at ansp.org> wrote:
> As Andy points out, there's a major difference between a fire 
 involving ethanol and one fueled by, say, gasoline - ethanol is 
 diluted by water, not carried by it. You won't spread an alcohol fire 
 by spraying large amounts of water on it, you'll put it out.
 
 PC.
 
 
 Paul Callomon
 Collections Manager in Malacology, Invertebrate Paleontology and 
 General Invertebrates The Academy of Natural Sciences of Drexel 
 University 1900 Benjamin Franklin Parkway Philadelphia, PA  19103 
 callomon at ansp.org Tel. 215-405-5096 ansp.org Follow us: 
 Facebook<http://www.facebook.com/AcademyofNaturalSciences>
 | Twitter<http://twitter.com/#!/AcadNatSci> Join us as we celebrate
 the Academy's 200th anniversary with a year of exciting events, 
 special programs, and our bicentennial exhibit, The Academy at 200:
 The Nature of Discovery. www.ansp.org<http://www.ansp.org>
 
 
 
 
 From: nhcoll-l-bounces at mailman.yale.edu 
 [mailto:nhcoll-l-bounces at mailman.yale.edu] On Behalf Of Bentley, 
 Andrew Charles Sent: Thursday, May 10, 2012 9:45 AM To: Gali Beiner; 
 nhcoll-l at mailman.yale.edu Subject: Re: [Nhcoll-l] Sprinklers in wet 
 collections
 
 Hi Gali
 
 I think the issue with water sprinklers spreading a fire are a little 
 overblown personally.  Her at the University of Kansas, Biodiversity 
 Institute we had a new facility for our wet collections built in the 
 mid 90's and we went with a three pronged solution:
 
 
 1.      Lowered temperature - 65°F - below the flash point of 70%
 ethanol which is 70°F
 
 2.      HVAC system that replaces air every two hours in the facility
 to prevent vapor buildup, and
 
 3.      A sprinkler system and smoke detectors.
 
 Personally I think the potential hazard to people of any gas 
 replacement system (CO2 or otherwise) and the additional cost (very 
 expensive initially and to maintain) far outweighs any potential issue 
 with a sprinkler system.  70% ethanol would be diluted so quickly that 
 it would have very little chance to spread dramatically within a 
 facility in the event of a fire.
 
 Hope that helps
 
 Andy
 
     A  :             A  :             A  :
  }<(((_°>.,.,.,.}<(((_°>.,.,.,.}<)))_°>
     V                V                V
  Andy Bentley
  Ichthyology Collection Manager
  University of Kansas
 Biodiversity Institute
  Dyche Hall
  1345 Jayhawk Boulevard
  Lawrence, KS, 66045-7561
  USA
 
 Tel: (785) 864-3863
 Fax: (785) 864-5335
  Email: abentley at ku.edu<mailto:abentley at ku.edu>
 http://ichthyology.biodiversity.ku.edu
                            :                 :
     A  :             A  :             A  :
  }<(((_°>.,.,.,.}<(((_°>.,.,.,.}<)))_°>
     V                V                V
 
 From:
 nhcoll-l-bounces at mailman.yale.edu<mailto:nhcoll-l-bounces at mailman.yale
 .edu> [mailto:nhcoll-l-bounces at mailman.yale.edu] On Behalf Of Gali 
 Beiner
 Sent: Thursday, May 10, 2012 1:06 AM To:
 nhcoll-l at mailman.yale.edu<mailto:nhcoll-l at mailman.yale.edu> Subject:
 [Nhcoll-l] Sprinklers in wet collections
 
 Dear Colleagues,
 
 We are currently dealing with a proposal to install water sprinklers 
 in our wet collection storage facilities as part of the general fire 
 hazard measures. It will be very helpful to know what kind of 
 fire-extinguishing measures have been installed in other facilities 
 holding jars and containers with alcohol / formalin / other 
 preservative fluids. Were there any particular considerations your 
 institute took into accound, given that preservation fluids tend to be 
 so flammable?
 
 Many thanks for your thoughts on this subject,
 
 Gali Beiner (ACR)
 Conservator, Palaeontology Lab
 National Natural History Collections
 The Hebrew University of Jerusalem
 Berman Building, Edmond J. Safra campus, Givat Ram Jerusalem 91904, 
 Israel Fax. 972-2-6584741 
 galib at savion.huji.ac.il<mailto:galib at savion.huji.ac.il>
 
 Look into our National Natural History Collections 
 <http://nnhc.huji.ac.il/default.asp?PageID=8> Website!

-
aul J. Morris
iodiversity Informatics Manager
arvard University Herbaria/Museum of Comparative Zoölogy mole at morris.net  AA3SD  
GP public key available _______________________________________________
hcoll-l mailing list
hcoll-l at mailman.yale.edu
ttp://mailman.yale.edu/mailman/listinfo/nhcoll-l
_______________________________________________
hcoll-l mailing list
hcoll-l at mailman.yale.edu
ttp://mailman.yale.edu/mailman/listinfo/nhcoll-l

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://mailman.yale.edu/pipermail/nhcoll-l/attachments/20120511/79654c48/attachment.html 


More information about the Nhcoll-l mailing list